KC868-a6-v1.3sp + 0.5V Analog Input - Printable Version +- Smart Home Automation Forum (https://www.kincony.com/forum) +-- Forum: Technical Support (https://www.kincony.com/forum/forumdisplay.php?fid=1) +--- Forum: KC868-A series and Uair Smart Controller (https://www.kincony.com/forum/forumdisplay.php?fid=6) +--- Thread: KC868-a6-v1.3sp + 0.5V Analog Input (/showthread.php?tid=8107) |
KC868-a6-v1.3sp + 0.5V Analog Input - boneless - 05-23-2025 Hello again, I have the KC868-a6-v1.3sp and a pressure sensor (0..150 psi / 0.5..4.5 V). I noticed my values were being capped at about 40 psi / 1.5 V. I verified with my fluke loop calibrator, and indeed have a limit at 1.5 V. The image below shows the raw value being capped at 1.01. I tried moving the input to the second, but I received the exact same values (capped). Below code is used for both test with input 36 and 39. You have any recommendations Code: RE: KC868-a6-v1.3sp + 0.5V Analog Input - admin - 05-24-2025 you can see this code for analog 0-5v input. Code: - platform: adcRE: KC868-a6-v1.3sp + 0.5V Analog Input - boneless - 05-24-2025 Ah yes, I must have missed the attenuation. Thank you so much, my apologies. |