24V Pulse input
#1
I have a IFM SM7000 flow meter that is set to nPn pulse output for measuring the flow unit.

It is a 24V unit (both the F16 and the flow meter)

What input on the F16 can I wire this to in order to count the pulses..... Will the standard digital inputs work?


Thanks
Reply
#2
you can connect with free GPIO port, config by ESPHome. not use by digital input, because digital input port with opto-coupler on PCB.
free GPIO are connect with ESP32S3 module pin directly.
Reply
#3
Hello Sir

I just want to understand, why should I not use the digital input port if it is opto-isolated???? Wouldnt that be safer/better becasue it is opto-isolated?
Reply
#4
i don't know your pulse whether is very fast. if not very fast, you can connect with digital input with opto-isolated.
Reply