10-13-2025, 02:04 AM
N10 Energy Module Modbus Protocol Specification
1. Overview
This document specifies the Modbus communication protocol for the N10 Energy Module.
The device communicates using the Modbus RTU protocol and provides access to electrical
measurement parameters including current, power, energy consumption, voltage, frequency,
temperature, and power factor.
2. Module Characteristics
- Energy Monitoring Chips: 1
- Communication Protocol: Modbus RTU
- Wireless Technology: Not applicable (wired connection)
- Maximum Sensors Supported: 32
- Board Features: Display, Ethernet (W5500), 4G, SD Card support
- GPIO Availability: 2 free GPIOs (pins 15, 16)
3. Communication Parameters
- Protocol: Modbus RTU
- Baud Rate: 38400
- Function Codes:
* 0x03: Read Holding Registers (for reading data)
* 0x05: Write Single Coil (for control operations)
* 0x10: Write Multiple Registers (for configuration)
4. Chip Addressing
The N10 Energy Module contains 1 measurement chip with base address:
| Chip Number | Base Address | Physical Location |
| Chip 1 | 100 | Main board |
5. Data Structure
The chip provides the following data (accessible via Function Code 0x03):
5.1 Current Measurements (RMS)
| Register Offset| Parameter | Units | Format | Resolution |
| 0 | RMS_1 | A | uint32 | 0.001A/LSB |
| 2 | RMS_2 | A | uint32 | 0.001A/LSB |
| 4 | RMS_3 | A | uint32 | 0.001A/LSB |
| 6 | RMS_4 | A | uint32 | 0.001A/LSB |
| 8 | RMS_5 | A | uint32 | 0.001A/LSB |
| 10 | RMS_6 | A | uint32 | 0.001A/LSB |
| 12 | RMS_7 | A | uint32 | 0.001A/LSB |
| 14 | RMS_8 | A | uint32 | 0.001A/LSB |
| 16 | RMS_9 | A | uint32 | 0.001A/LSB |
| 18 | RMS_10 | A | uint32 | 0.001A/LSB |
Example: To read RMS_1 from Chip 1, read registers 100 and 101 (2 registers for uint32).
Display: Reading of 5432 represents 5.432A (5432 × 0.001A)
5.2 Power Measurements (WATT)
| 20 | WATT_1 | W | uint32 | 0.1W/LSB |
| 22 | WATT_2 | W | uint32 | 0.1W/LSB |
| 24 | WATT_3 | W | uint32 | 0.1W/LSB |
| 26 | WATT_4 | W | uint32 | 0.1W/LSB |
| 28 | WATT_5 | W | uint32 | 0.1W/LSB |
| 30 | WATT_6 | W | uint32 | 0.1W/LSB |
| 32 | WATT_7 | W | uint32 | 0.1W/LSB |
| 34 | WATT_8 | W | uint32 | 0.1W/LSB |
| 36 | WATT_9 | W | uint32 | 0.1W/LSB |
| 38 | WATT_10 | W | uint32 | 0.1W/LSB |
Example: To read WATT_1 from Chip 1, read registers 120 and 121 (2 registers for uint32).
Display: Reading of 12345 represents 1234.5W (12345 × 0.1W)
5.3 Energy Consumption Measurements
| 40 | Energy_1 | kWh | uint32 | 1kWh/LSB |
| 42 | Energy_2 | kWh | uint32 | 1kWh/LSB |
| 44 | Energy_3 | kWh | uint32 | 1kWh/LSB |
| 46 | Energy_4 | kWh | uint32 | 1kWh/LSB |
| 48 | Energy_5 | kWh | uint32 | 1kWh/LSB |
| 50 | Energy_6 | kWh | uint32 | 1kWh/LSB |
| 52 | Energy_7 | kWh | uint32 | 1kWh/LSB |
| 54 | Energy_8 | kWh | uint32 | 1kWh/LSB |
| 56 | Energy_9 | kWh | uint32 | 1kWh/LSB |
| 58 | Energy_10 | kWh | uint32 | 1kWh/LSB |
| 60 | Energy_Sum | kWh | uint32 | 1kWh/LSB |
Note: The maximum measurable energy per channel is 65535 kWh.
5.4 Other Measurements
| 62 | RMS_V | V | uint16 | 0.01V/LSB |
| 63 | Period | Hz | uint16 | 0.01Hz/LSB |
| 64 | TPS1 | °C | float | 0.1°C/LSB |
| 66 | PF | - | float | Power Factor (0-1) |
6. Control Functions (Function Code 0x05)
The following control registers can be written to using the Modbus function code 0x05:
| Register | Function | Description |
| 500 | Warm Reset | Resets the device |
| 501 | Save Parameters to Flash | Save communication parameters to flash |
| 503 | Save Coefficients to Flash | Save calibration coefficients to flash |
| 504 | Clear Coefficients | Reset all coefficients to 1.0 (use caution)|
| 510 | Restore Factory Settings | Restore factory communication parameters |
7. Energy Clearing Functions (Function Code 0x05)
The following registers clear energy consumption data when written with function code 0x05:
7.1 Clear All Channels on the Chip
| 520 | Clear all energy on Chip 1 |
7.2 Clear Individual Channels
| Register Range | Function |
| 526-535 | Clear energy on Chip 1, channels 1-10 |
| 586 | Clear sum energy on Chip 1 |
8. Calibration Coefficients (Function Code 0x03 to read, 0x10 to write)
All coefficients are stored as floating-point values in CDBA format.
8.1 Current (RMS) Coefficients for Chip 1
| Register | Parameter | Default |
| 3000 | FACTOR OF RMS1 | 1.0 |
| 3002 | FACTOR OF RMS2 | 1.0 |
| 3004 | FACTOR OF RMS3 | 1.0 |
| 3006 | FACTOR OF RMS4 | 1.0 |
| 3008 | FACTOR OF RMS5 | 1.0 |
| 3010 | FACTOR OF RMS6 | 1.0 |
| 3012 | FACTOR OF RMS7 | 1.0 |
| 3014 | FACTOR OF RMS8 | 1.0 |
| 3016 | FACTOR OF RMS9 | 1.0 |
| 3018 | FACTOR OF RMS10 | 1.0 |
8.2 Power (WATT) Coefficients for Chip 1
| 3020 | FACTOR OF WATT1 | 1.0 |
| 3022 | FACTOR OF WATT2 | 1.0 |
| 3024 | FACTOR OF WATT3 | 1.0 |
| 3026 | FACTOR OF WATT4 | 1.0 |
| 3028 | FACTOR OF WATT5 | 1.0 |
| 3030 | FACTOR OF WATT6 | 1.0 |
| 3032 | FACTOR OF WATT7 | 1.0 |
| 3034 | FACTOR OF WATT8 | 1.0 |
| 3036 | FACTOR OF WATT9 | 1.0 |
| 3038 | FACTOR OF WATT10 | 1.0 |
8.3 Energy Coefficients for Chip 1
| 3040 | FACTOR OF ENERGY1 | 1.0 |
| 3042 | FACTOR OF ENERGY2 | 1.0 |
| 3044 | FACTOR OF ENERGY3 | 1.0 |
| 3046 | FACTOR OF ENERGY4 | 1.0 |
| 3048 | FACTOR OF ENERGY5 | 1.0 |
| 3050 | FACTOR OF ENERGY6 | 1.0 |
| 3052 | FACTOR OF ENERGY7 | 1.0 |
| 3054 | FACTOR OF ENERGY8 | 1.0 |
| 3056 | FACTOR OF ENERGY9 | 1.0 |
| 3058 | FACTOR OF ENERGY10 | 1.0 |
| 3060 | FACTOR OF ENERGY SUM | 1.0 |
9. Programming Notes
1. After modifying communication parameters, write to register 501 to save them to flash.
2. After modifying calibration coefficients, write to register 503 to save them to flash.
3. Read the entire data structure for the chip by reading 68 registers starting at base
address 100.
4. For 32-bit values (uint32, float), read/write two consecutive registers.
5. When writing float values, use the CDBA format.
6. All energy measurements have a maximum value of 65535 kWh per channel.
10. Comparison with Other N-Series Modules
| Feature | N10 | N20 | N30 |
| Communication | Modbus RTU | Modbus RTU | Modbus RTU |
| Energy Chips | 1 | 2 | 3 |
| Channels | 10 | 20 | 30 |
| Base Addresses | 100 | 100, 200 | 100, 200, 300 |
| Data Structure | Standard | Dual-chip | Triple-chip |
| Installation | Wired | Wired | Wired |
11. Conclusion
The N10 Energy Module provides single-chip energy monitoring with Modbus RTU
communication, making it ideal for small-scale installations requiring precise
electrical measurement and monitoring. The device offers 10 channels of current,
power, and energy monitoring with comprehensive calibration and control capabilities.
Document generated for N10 Energy Module Modbus Protocol
For technical support, please contact Kincony support team.
N10_Energy_Modbus_Protocol.txt (Size: 11.62 KB / Downloads: 193)