"KCS" v3 TCP/IP Standard Modbus protocol document
#1
KCS protocol webpage, "TCP Server" = "Modbus TCP". it's a standard modbus protocol.
Code:
KCSv3 Modbus TCP Protocol Specification
=======================================

1. Overview
-----------

This document specifies the standard Modbus TCP protocol exposed by the
KCSv3 firmware TCP server.

This mode uses the standard Modbus TCP ADU with an MBAP header. It does not use
the RTU CRC field.

2. Communication Parameters
---------------------------

- Protocol: Standard Modbus TCP
- TCP port: configured by tcp_server_port
- Unit ID: configured by tcp_server_protocol_modbus_local_addr
- Register addressing: 0-based Modbus protocol address
- Frame format: [MBAP Header][PDU]
- Protocol ID in MBAP: 0x0000
- CRC: not used

MBAP header format:

+--------+----------------+----------------------------------------------+
| Bytes  | Field          | Description                                  |
+--------+----------------+----------------------------------------------+
| 0..1   | Transaction ID | Echoed in the response                       |
| 2..3   | Protocol ID    | Must be 0x0000                               |
| 4..5   | Length         | Unit ID byte + PDU length                    |
| 6      | Unit ID        | Must match tcp_server_protocol_modbus_local_addr |
+--------+----------------+----------------------------------------------+

The firmware validates the MBAP Protocol ID, Length, and Unit ID before
processing the PDU. Responses are sent only to the requesting TCP client.

3. Supported Function Codes
---------------------------

+---------------+---------------------------+-------------------------------+
| Function Code | Name                      | Usage                         |
+---------------+---------------------------+-------------------------------+
| 0x01          | Read Coils                | Read DO output state          |
| 0x02          | Read Discrete Inputs      | Read DI input state           |
| 0x03          | Read Holding Registers    | Read DAC/IR/RF/energy data    |
| 0x04          | Read Input Registers      | Read ADC/temperature/humidity |
| 0x05          | Write Single Coil         | Set one DO or trigger toggle  |
| 0x06          | Write Single Register     | Set DAC or trigger IR/RF      |
| 0x0F          | Write Multiple Coils      | Set multiple DO channels      |
| 0x10          | Write Multiple Registers  | Set multiple DAC channels     |
+---------------+---------------------------+-------------------------------+

4. Addressing Notes
-------------------

All addresses in this document are 0-based Modbus protocol addresses.

Examples:

- Holding register address 100 is sent as 0x0064 in the Modbus PDU.
- In pymodbus, use read_holding_registers(100, count=2, slave=<unit_id>).
- Some Modbus tools display holding register 100 as 40101 or similar. Use the
  tool's 0-based/1-based setting carefully.

5. Coils (Function Codes 0x01, 0x05, 0x0F)
-------------------------------------------

5.1 DO Output State and Control
-------------------------------

+------------------------+----------------------+-----------------------------+
| Address Range          | Description          | Access                      |
+------------------------+----------------------+-----------------------------+
| 0 .. DO_NUM-1          | DO output channels   | 0x01 read, 0x05/0x0F write  |
+------------------------+----------------------+-----------------------------+

Write value for function code 0x05:

- 0xFF00: turn ON
- 0x0000: turn OFF

Function code 0x0F supports only the normal DO output range starting at address
0.

5.2 DO Toggle Control
---------------------

+-----------------------------+----------------------+--------------------------+
| Address Range               | Description          | Access                   |
+-----------------------------+----------------------+--------------------------+
| 0x0100 .. 0x0100+DO_NUM-1   | Toggle DO channels   | 0x05 write only          |
+-----------------------------+----------------------+--------------------------+

Write 0xFF00 to address 0x0100 + channel_index to toggle that output channel.
Writing 0x0000 is accepted but does not toggle the output.

6. Discrete Inputs (Function Code 0x02)
---------------------------------------

+------------------------+----------------------+-----------------------------+
| Address Range          | Description          | Access                      |
+------------------------+----------------------+-----------------------------+
| 0 .. DI_NUM-1          | DI input channels    | 0x02 read                   |
+------------------------+----------------------+-----------------------------+

DI inputs are active-low in the firmware mapping:

- Hardware low / active input returns 1
- Hardware high / inactive input returns 0

7. Holding Registers (Function Codes 0x03, 0x06, 0x10)
------------------------------------------------------

7.1 DAC Output Registers
------------------------

+------------------------+----------------------+-----------------------------+
| Address Range          | Description          | Access                      |
+------------------------+----------------------+-----------------------------+
| 0 .. DAC_NUM-1         | DAC output channels  | 0x03 read, 0x06/0x10 write  |
+------------------------+----------------------+-----------------------------+

DAC write value range: 0 .. 255.

Function code 0x10 supports only this DAC register range.

7.2 IR/RF Control Registers
---------------------------

+----------+-------------+----------------------+-----------------------------+
| Address  | Name        | Description          | Access                      |
+----------+-------------+----------------------+-----------------------------+
| 0x0040   | IR_SEND     | Send learned IR slot | 0x03 read, 0x06 write       |
| 0x0041   | IR_LEARN    | Learn IR slot/port   | 0x03 read, 0x06 write       |
| 0x0042   | IR_DELETE   | Delete IR slot       | 0x03 read, 0x06 write       |
| 0x0050   | RF_SEND     | Send learned RF slot | 0x03 read, 0x06 write       |
+----------+-------------+----------------------+-----------------------------+

IR_SEND:

- Value: IR memory slot index
- Valid range: 0 .. IR_MEM_NUM-1

IR_LEARN:

- High byte: IR memory slot index
- Low byte: IR send port number, starting from 1

IR_DELETE:

- Value: IR memory slot index
- Valid range: 0 .. IR_MEM_NUM-1

RF_SEND:

- Value: RF memory slot index
- The selected RF slot must exist and be learned

These registers exist only on board variants with the corresponding IR/RF
feature enabled. Otherwise accesses return an illegal data address exception.

7.3 Energy Measurement Registers
--------------------------------

Energy data is exposed as read-only Holding Registers and is read with function
code 0x03.

Each energy chip uses 68 holding registers. The base address is:

  base = 100 + chip_index * 100

where chip_index starts from 0.

+--------------+----------------+----------------+--------------------------+
| Offset Range | Parameter      | Format         | Resolution / Notes       |
+--------------+----------------+----------------+--------------------------+
| 0 .. 19      | RMS_1..RMS_10  | uint32 CDAB    | Current in A * 1000      |
| 20 .. 39     | WATT_1..WATT_10| int32 CDAB     | Power in W * 10          |
| 40 .. 59     | Energy_1..10   | float32 CDAB   | Energy in kWh            |
| 60 .. 61     | Energy_Sum     | float32 CDAB   | Total energy in kWh      |
| 62           | RMS_V          | uint16         | Voltage in V * 100       |
| 63           | Period         | uint16         | Frequency in Hz * 100    |
| 64 .. 65     | TPS1           | float32 CDAB   | Temperature in deg C     |
| 66 .. 67     | PF             | float32 CDAB   | Power factor             |
+--------------+----------------+----------------+--------------------------+

Per-channel offsets:

+----------------+----------------+----------------+--------------------------+
| Channel        | Current Offset | Power Offset   | Energy Offset            |
+----------------+----------------+----------------+--------------------------+
| 1              | 0              | 20             | 40                       |
| 2              | 2              | 22             | 42                       |
| 3              | 4              | 24             | 44                       |
| 4              | 6              | 26             | 46                       |
| 5              | 8              | 28             | 48                       |
| 6              | 10             | 30             | 50                       |
| 7              | 12             | 32             | 52                       |
| 8              | 14             | 34             | 54                       |
| 9              | 16             | 36             | 56                       |
| 10             | 18             | 38             | 58                       |
+----------------+----------------+----------------+--------------------------+

For 32-bit integer and float values, read two consecutive registers. The lower
16-bit word is returned first, followed by the upper 16-bit word.

Examples:

- Chip 1 current channel 1: read holding registers 100 and 101
- Chip 2 power channel 1: read holding registers 220 and 221
- Chip 1 voltage: read holding register 162
- Chip 1 frequency: read holding register 163

8. Input Registers (Function Code 0x04)
---------------------------------------

+-------------------------------+----------------------+--------------------------+
| Address Range                 | Description          | Format                   |
+-------------------------------+----------------------+--------------------------+
| 0 .. ADC_NUM-1                | ADC input channels   | uint16 raw ADC value     |
| 0x0100 .. 0x0100+SENSOR_NUM-1 | Temperature sensors  | int16, deg C * 10        |
| 0x0120 .. 0x0120+SENSOR_NUM-1 | Humidity sensors     | int16, %RH * 10          |
+-------------------------------+----------------------+--------------------------+

If a temperature or humidity sensor is invalid or not present, the returned
value is 0x7FFF.

9. Board-Dependent Limits
-------------------------

The following symbols depend on the compiled board model:

- DO_NUM: number of digital outputs
- DI_NUM: number of digital inputs
- DAC_NUM: number of DAC outputs
- ADC_NUM: number of ADC inputs
- SENSOR_NUM: maximum temperature/humidity sensor slots
- ENERGY_NUM: number of energy measurement chips

N-series energy chip bases:

+-------+------------+--------------------------------------+
| Board | ENERGY_NUM | Energy Holding Register Bases        |
+-------+------------+--------------------------------------+
| N10   | 1          | 100                                  |
| N20   | 2          | 100, 200                             |
| N30   | 3          | 100, 200, 300                        |
| N60   | 6          | 100, 200, 300, 400, 500, 600         |
+-------+------------+--------------------------------------+

10. Exception Codes
-------------------

+----------------+----------------------------+-------------------------------+
| Exception Code | Name                       | Meaning                       |
+----------------+----------------------------+-------------------------------+
| 0x01           | Illegal Function           | Unsupported function code     |
| 0x02           | Illegal Data Address       | Unsupported address/range     |
| 0x03           | Illegal Data Value         | Invalid value or quantity     |
| 0x04           | Slave Device Failure       | Runtime failure or overflow   |
+----------------+----------------------------+-------------------------------+

11. Request Size Limits
-----------------------

- Read coils/discrete inputs: quantity 1 .. 2000
- Read holding/input registers: quantity 1 .. 125
- Write multiple coils: quantity 1 .. 1968
- Write multiple registers: quantity 1 .. 123
download protocol:

.txt   Modbus_TCP_Protocol.txt (Size: 11.59 KB / Downloads: 13)