Hi,

I am trying to get the N30 to work as a modbus device that I can read from via TCP on port 502. Could not get it to work on the IP address of the N30

Hooked up a Hi-Flying EW11 TCP to modbus converter to the RS485 port in modbus mode and that does work. Can see all the registers for chips on address 100/200/300
I was assuming that the setting

TCP Server: enable
Protocol:     Modbus
local port:   502
modbus local addr 1

Would be sufficient to read the registers via the N30 IP address on port 502

Whatever I try I do get a time-out

Port 502 is open if I test with ModbusDoctor or Powershell I get connected but no readings at the expected adresses.

Also tried with setting Modbus-RTU-v2 and a virtual COM port without any responce. Please provide instructions if this should work and if so how?

Thanks,
GWS
Reply
#2
you can read N30 by RS485 modbus protocol, not support TCP modbus by network.
Reply
#3
If that is the case I don't understand what this setting is for (of Modbus does not work)

   

Looked to me like this was intended to make the N30 respond like a Modbus device. Is this only for communication with a modbus device?

Thanks,
GWS
Reply
#4
N series board not support TCP modbus, but we can update for it. in future will add TCP modbus.
Reply
#5
here is new firmware for N series board supoprt TCP modbus now.

1. Modbus_RTU_Protocol: serial modbus protocol use by RS485 "Modbus-RTU-v2"
2. Modbus_RTU_over_TCP_Protocol: tcp modbus rtu protocol,KCS webpapge protocol -- tcp server -- "Modbus-RTU-v2" option.
3. Modbus_TCP_Protocol: tcp standard modbus protocol,KCS webpage protocol -- tcp server "Modbus TCP" option.


Attached Files
.zip   KCS_N30_V3.25.1_beta_20260523-034001.zip (Size: 1.03 MB / Downloads: 180)
.txt   Modbus_RTU_over_TCP_Protocol.txt (Size: 11.05 KB / Downloads: 91)
.txt   Modbus_RTU_Protocol.txt (Size: 10.7 KB / Downloads: 85)
.txt   Modbus_TCP_Protocol.txt (Size: 11.59 KB / Downloads: 105)