Yesterday, 09:27 AM
Hi,
I see some weird bahavior on my N30 that I do not understand:
Using CT with factor 1000:1 and after measering the actual curren with MID approved device I found that factor 2.1 was the best.
When I save the factor 2.1 it results in 2.0999... etc and that might very well be because of how the factor is binary processed in the chip.
So initially I started with setting all factors to 2.1 (for testing I have now set CH01 to factor 2 and CH02 to 1)
But on Channel 2 (first 901 chip) I got strange values and the Power Factor keeps changing in the header of the dat for that chip.
On the other two chips it stays on 1.0000 and the data looked correct.
When I move the CT connector for 1..10 to the position of the 11..20 I see that CH12 is displaying the expected values.
Looks like CHIP 1 is behaving differtent from CHIP 2&3.
Any idea what could cause this?
Related to this I would like to know how to best set the factors I it necessary to set all columns with same factor? (Please provide a field for the default setting for all columns)
Power = Voltage * Current
Energy = Power over time accumulated. It is not fully clear if I need the factor (2.1) there also, or should it be 1 since the power is already corrected.
Thanks,
GWS
I see some weird bahavior on my N30 that I do not understand:
Using CT with factor 1000:1 and after measering the actual curren with MID approved device I found that factor 2.1 was the best.
When I save the factor 2.1 it results in 2.0999... etc and that might very well be because of how the factor is binary processed in the chip.
So initially I started with setting all factors to 2.1 (for testing I have now set CH01 to factor 2 and CH02 to 1)
But on Channel 2 (first 901 chip) I got strange values and the Power Factor keeps changing in the header of the dat for that chip.
On the other two chips it stays on 1.0000 and the data looked correct.
When I move the CT connector for 1..10 to the position of the 11..20 I see that CH12 is displaying the expected values.
Looks like CHIP 1 is behaving differtent from CHIP 2&3.
Any idea what could cause this?
Related to this I would like to know how to best set the factors I it necessary to set all columns with same factor? (Please provide a field for the default setting for all columns)
Power = Voltage * Current
Energy = Power over time accumulated. It is not fully clear if I need the factor (2.1) there also, or should it be 1 since the power is already corrected.
Thanks,
GWS