(Yesterday, 07:47 PM)admin Wrote: you should chose 2000:1 CT sensor, suggest you buy CT sensor from KinCony online shop.
Ok this I can understand however since I have already 16 of them and the problem is that I'm not receiving at all measurements I need to figure out whether there is somewhere else the problem.
Wven with 1800:1 turn ratio the sensor should measure bigger Amperage then the 2000:1 and with the same burden resistance to give more than 1V measurement to the controller (when it measures 50Amp , the maximum possible measurement). In my case Im not receiving measurements at all... like the sensors are not operating or the controller is not logging the measurements.
Tks a lot.