N30 + KCS v3.15.0 firmware
Hello.
I bought N30. Download and write KCS v3.15.0 firmware for N30.
Some observations.
After changing Current Factor to take effect Reset ARM CPU button must be pressed.
Current Factor:
In youtube video Current Factor mean:
Value*CurrentFactor=desired value.
It's not TRUE. It works like:
Value/CurrentFactor=desired value.
[Image: N30-04.webp]
[Image: N30-01.webp]
I use CT 3000/1 and need to correct values. N30 gives 0.12A instead real value is about 0.17A
Next one. I connect to N2L2 to power source.
[Image: N30-02.webp]
[Image: N30-03.webp]
And I have Power Factor is 0.00. Is it correct?
Voltage and 228.9Frequency are shown correctly.
Best wishes.
how do you connect with your load. can you take a photo.
All CT clamps is on line wire (220v 50hz).
Chip1
CH1 - CT 20A 2000/1
CH2 - CT 60A 2000/1
Chip2
CH1 - CT 20A 2000/1
CH2 - CT 20A 2000/1
CH3 - CT 20A 2000/1
CH4 - CT 20A 2000/1
CH5 - CT 20A 2000/1
CH6 - CT 20A 2000/1
Chip3
CH1 - CT 140A 3000/1
CH2 - CT 140A 3000/1
CH3 - CT 140A 3000/1
CH4 - CT 140A 3000/1
CH5 - CT 140A 3000/1
CH6 - CT 140A 3000/1
Chip2
L2N2 connected to same power source 220v 50hz
you have only connect voltage for L2 and L1. you need connect with all, L1=L2=L3, N1=N2=N3. because every BL0910 energy chip need voltage to calculate all data.
Thanks. Will test.