04-01-2025, 01:31 PM
Is it possible to connect an analog sensor with a 4-20mA output to the KC868-A16? Some say only 0-5V and some say both. If so, how please? Thanks.
KC868-A16 analog input
04-01-2025, 11:55 PM
KC868-A16 board: analog input: A1,A2 for 4-20mA A3,A4 for 0-5v dc
I have four three-phase motors and I need to read one phase of each motor. I am using the KC868-a16 and the JXK-10 CTs, two with 4-20mA output and two with 0-5V output.
The CTs have two inputs for 24V +/- power supply and two +/- 4-20mA or 0-5V outputs. In this project, I joined the "Out -" outputs of the four CTs and connected them to the analog GND of the KC868-a16. The "Out +" outputs were connected to each specific 4-20mA input A1, A2 and 0-5V A3, A4. Is this connection correct? KC868-a16 TC.jpg
04-02-2025, 10:18 PM
KC868-A16 not support CT clamp sensor. you need use M30 board for CT clamp.
I made the connections and it's working!
The CT I'm using has a 4-20mA or 0-5V output and not AC voltage. https://pt.aliexpress.com/item/100500613...ry_from%3A - platform: adc pin: 34 name: "A16 A2 mA" update_interval: 5s attenuation: 12db unit_of_measurement: mA filters: - multiply: 6.66666666
04-04-2025, 12:10 AM
ok, i see now, you are using DC CT sensor.
« Next Oldest | Next Newest »