KCS protocol webpage, set to "Modbus_RTU-v2" option. it's a standard modbus protocol.
download protocol:
Modbus_RTU_Protocol.txt (Size: 10.7 KB / Downloads: 47)
KCSv3 Modbus RTU Protocol Specification
1. Overview
This document specifies the Modbus RTU protocol exposed by the KCSv3
firmware on the RS485 interface.
2. Communication Parameters
- Protocol: Modbus RTU
- Physical interface: RS485
- Slave address: configured by rs485_local_addr
- Register addressing: 0-based Modbus protocol address
- Frame format: [Slave Address][PDU][CRC Lo][CRC Hi]
- CRC: Modbus CRC16, low byte first
Serial port parameters are configured by the firmware RS485 settings.
3. Supported Function Codes
| Function Code | Name | Usage |
| 0x01 | Read Coils | Read DO output state |
| 0x02 | Read Discrete Inputs | Read DI input state |
| 0x03 | Read Holding Registers | Read DAC/IR/RF/energy data |
| 0x04 | Read Input Registers | Read ADC/temperature/humidity |
| 0x05 | Write Single Coil | Set one DO or trigger toggle |
| 0x06 | Write Single Register | Set DAC or trigger IR/RF |
| 0x0F | Write Multiple Coils | Set multiple DO channels |
| 0x10 | Write Multiple Registers | Set multiple DAC channels |
4. Addressing Notes
All addresses in this document are 0-based Modbus protocol addresses.
Examples:
- Holding register address 100 is sent as 0x0064 in the Modbus PDU.
- Some Modbus tools display holding register 100 as 40101 or similar. Use the
tool's 0-based/1-based setting carefully.
5. Coils (Function Codes 0x01, 0x05, 0x0F)
5.1 DO Output State and Control
| Address Range | Description | Access |
| 0 .. DO_NUM-1 | DO output channels | 0x01 read, 0x05/0x0F write |
Write value for function code 0x05:
- 0xFF00: turn ON
- 0x0000: turn OFF
Function code 0x0F supports only the normal DO output range starting at address
0.
5.2 DO Toggle Control
| 0x0100 .. 0x0100+DO_NUM-1 | Toggle DO channels | 0x05 write only |
Write 0xFF00 to address 0x0100 + channel_index to toggle that output channel.
Writing 0x0000 is accepted but does not toggle the output.
6. Discrete Inputs (Function Code 0x02)
| 0 .. DI_NUM-1 | DI input channels | 0x02 read |
DI inputs are active-low in the firmware mapping:
- Hardware low / active input returns 1
- Hardware high / inactive input returns 0
7. Holding Registers (Function Codes 0x03, 0x06, 0x10)
7.1 DAC Output Registers
| 0 .. DAC_NUM-1 | DAC output channels | 0x03 read, 0x06/0x10 write |
DAC write value range: 0 .. 255.
Function code 0x10 supports only this DAC register range.
7.2 IR/RF Control Registers
| Address | Name | Description | Access |
| 0x0040 | IR_SEND | Send learned IR slot | 0x03 read, 0x06 write |
| 0x0041 | IR_LEARN | Learn IR slot/port | 0x03 read, 0x06 write |
| 0x0042 | IR_DELETE | Delete IR slot | 0x03 read, 0x06 write |
| 0x0050 | RF_SEND | Send learned RF slot | 0x03 read, 0x06 write |
IR_SEND:
- Value: IR memory slot index
- Valid range: 0 .. IR_MEM_NUM-1
IR_LEARN:
- High byte: IR memory slot index
- Low byte: IR send port number, starting from 1
IR_DELETE:
RF_SEND:
- Value: RF memory slot index
- The selected RF slot must exist and be learned
These registers exist only on board variants with the corresponding IR/RF
feature enabled. Otherwise accesses return an illegal data address exception.
7.3 Energy Measurement Registers
Energy data is exposed as read-only Holding Registers and is read with function
code 0x03.
Each energy chip uses 68 holding registers. The base address is:
base = 100 + chip_index * 100
where chip_index starts from 0.
| Offset Range | Parameter | Format | Resolution / Notes |
| 0 .. 19 | RMS_1..RMS_10 | uint32 CDAB | Current in A * 1000 |
| 20 .. 39 | WATT_1..WATT_10| int32 CDAB | Power in W * 10 |
| 40 .. 59 | Energy_1..10 | float32 CDAB | Energy in kWh |
| 60 .. 61 | Energy_Sum | float32 CDAB | Total energy in kWh |
| 62 | RMS_V | uint16 | Voltage in V * 100 |
| 63 | Period | uint16 | Frequency in Hz * 100 |
| 64 .. 65 | TPS1 | float32 CDAB | Temperature in deg C |
| 66 .. 67 | PF | float32 CDAB | Power factor |
Per-channel offsets:
| Channel | Current Offset | Power Offset | Energy Offset |
| 1 | 0 | 20 | 40 |
| 2 | 2 | 22 | 42 |
| 3 | 4 | 24 | 44 |
| 4 | 6 | 26 | 46 |
| 5 | 8 | 28 | 48 |
| 6 | 10 | 30 | 50 |
| 7 | 12 | 32 | 52 |
| 8 | 14 | 34 | 54 |
| 9 | 16 | 36 | 56 |
| 10 | 18 | 38 | 58 |
For 32-bit integer and float values, read two consecutive registers. The lower
16-bit word is returned first, followed by the upper 16-bit word.
Examples:
- Chip 1 current channel 1: read holding registers 100 and 101
- Chip 2 power channel 1: read holding registers 220 and 221
- Chip 1 voltage: read holding register 162
- Chip 1 frequency: read holding register 163
8. Input Registers (Function Code 0x04)
| Address Range | Description | Format |
| 0 .. ADC_NUM-1 | ADC input channels | uint16 raw ADC value |
| 0x0100 .. 0x0100+SENSOR_NUM-1 | Temperature sensors | int16, deg C * 10 |
| 0x0120 .. 0x0120+SENSOR_NUM-1 | Humidity sensors | int16, %RH * 10 |
If a temperature or humidity sensor is invalid or not present, the returned
value is 0x7FFF.
9. Board-Dependent Limits
The following symbols depend on the compiled board model:
- DO_NUM: number of digital outputs
- DI_NUM: number of digital inputs
- DAC_NUM: number of DAC outputs
- ADC_NUM: number of ADC inputs
- SENSOR_NUM: maximum temperature/humidity sensor slots
- ENERGY_NUM: number of energy measurement chips
N-series energy chip bases:
| Board | ENERGY_NUM | Energy Holding Register Bases |
| N10 | 1 | 100 |
| N20 | 2 | 100, 200 |
| N30 | 3 | 100, 200, 300 |
| N60 | 6 | 100, 200, 300, 400, 500, 600 |
10. Exception Codes
| Exception Code | Name | Meaning |
| 0x01 | Illegal Function | Unsupported function code |
| 0x02 | Illegal Data Address | Unsupported address/range |
| 0x03 | Illegal Data Value | Invalid value or quantity |
| 0x04 | Slave Device Failure | Runtime failure or overflow |
11. Request Size Limits
- Read coils/discrete inputs: quantity 1 .. 2000
- Read holding/input registers: quantity 1 .. 125
- Write multiple coils: quantity 1 .. 1968
- Write multiple registers: quantity 1 .. 123