Maximum input current and voltage - Printable Version +- Smart Home Automation Forum (https://www.kincony.com/forum) +-- Forum: Technical Support (https://www.kincony.com/forum/forumdisplay.php?fid=20) +--- Forum: KC868-M16 / M1 / MB / M30 (https://www.kincony.com/forum/forumdisplay.php?fid=50) +--- Thread: Maximum input current and voltage (/showthread.php?tid=3426) |
Maximum input current and voltage - Wim - 10-25-2023 Hi, what are the maximum voltage and current that the inputs of the KC868-M16v2 accepts? I wish to know in order to select the most suitable CT-clamps for my power distribution box. If this is specified somewhere, I didn't find it. If so, where is the spec sheet that mentions these values? Thanks in advance RE: Maximum input current and voltage - admin - 10-26-2023 CT clamp sensor voltage range is dc 0-1v CT clamp sensor current range is 0-50mA RE: Maximum input current and voltage - Wim - 10-26-2023 Thanks for your answer. Your answer is not 100% what I asked. But I'm guessing the rest of the reasoning. Can you confirm? 25mA and 1V are also the maximum input current/voltage that should be applied to the bourd inputs? And therefore, selecting the right CT-clamp means that I need to select the CT-clamp with the lowest possible input current, which is higher than the highest current that I will ever monitor. Is that correct? Thanks again RE: Maximum input current and voltage - admin - 10-26-2023 50mA and 1V are also the maximum input current/voltage that should be applied to the board inputs? Yes, here is M16 diagram: https://www.kincony.com/download/KC868-M16-schematic.pdf |