Posts: 16
Threads: 2
Joined: Feb 2024
Reputation:
0
hi,
i'm trying to connect some solenoid valve to the board .
the solenoid use 24vac, when i connect the cable of the solenoid valve to the output 1, it goes on.
i don't undestand why
Posts: 6,686
Threads: 844
Joined: Oct 2020
Reputation:
162
take a photo, how you wire. A8M output DC voltage, but you are using AC solenid, how it works?
Posts: 6,686
Threads: 844
Joined: Oct 2020
Reputation:
162
No, it's wrong. you should connect a extend relay to control AC load (solenoid valve)
Posts: 16
Threads: 2
Joined: Feb 2024
Reputation:
0
then i have to move to k868 a8?.
but i don't understand why if it is a dry contact it can't use the vac
Posts: 6,686
Threads: 844
Joined: Oct 2020
Reputation:
162
A8 is relay , it's dry contact. A8M is MOSFET output, it work with DC voltage, not work for AC.