"KCS" v3 Modbus RTU over TCP/IP protocol document
#1
KCS protocol webpage, "TCP Server" = "Modbus-RTU-V2". Just RS485 modbus protocol over TCP/IP.
Code:
KCSv3 Modbus RTU over TCP Protocol Specification
================================================

1. Overview
-----------

This document specifies the Modbus RTU over TCP protocol exposed by the
KCSv3 firmware TCP server when the TCP protocol mode is configured for Modbus RTU
frames.

This mode transports a complete Modbus RTU ADU over a TCP socket. It does not use
the standard Modbus TCP MBAP header.

2. Communication Parameters
---------------------------

- Protocol: Modbus RTU ADU transported over TCP
- TCP port: configured by tcp_server_port
- Slave address: configured by tcp_server_protocol_modbus_local_addr
- Register addressing: 0-based Modbus protocol address
- Frame format: [Slave Address][PDU][CRC Lo][CRC Hi]
- CRC: Modbus CRC16, low byte first
- MBAP header: not used

Clients should send one complete RTU ADU frame per TCP request. The firmware
validates the RTU slave address and CRC before processing the PDU.

3. Supported Function Codes
---------------------------

+---------------+---------------------------+-------------------------------+
| Function Code | Name                      | Usage                         |
+---------------+---------------------------+-------------------------------+
| 0x01          | Read Coils                | Read DO output state          |
| 0x02          | Read Discrete Inputs      | Read DI input state           |
| 0x03          | Read Holding Registers    | Read DAC/IR/RF/energy data    |
| 0x04          | Read Input Registers      | Read ADC/temperature/humidity |
| 0x05          | Write Single Coil         | Set one DO or trigger toggle  |
| 0x06          | Write Single Register     | Set DAC or trigger IR/RF      |
| 0x0F          | Write Multiple Coils      | Set multiple DO channels      |
| 0x10          | Write Multiple Registers  | Set multiple DAC channels     |
+---------------+---------------------------+-------------------------------+

4. Addressing Notes
-------------------

All addresses in this document are 0-based Modbus protocol addresses.

Examples:

- Holding register address 100 is sent as 0x0064 in the Modbus PDU.
- Some Modbus tools display holding register 100 as 40101 or similar. Use the
  tool's 0-based/1-based setting carefully.

5. Coils (Function Codes 0x01, 0x05, 0x0F)
-------------------------------------------

5.1 DO Output State and Control
-------------------------------

+------------------------+----------------------+-----------------------------+
| Address Range          | Description          | Access                      |
+------------------------+----------------------+-----------------------------+
| 0 .. DO_NUM-1          | DO output channels   | 0x01 read, 0x05/0x0F write  |
+------------------------+----------------------+-----------------------------+

Write value for function code 0x05:

- 0xFF00: turn ON
- 0x0000: turn OFF

Function code 0x0F supports only the normal DO output range starting at address
0.

5.2 DO Toggle Control
---------------------

+-----------------------------+----------------------+--------------------------+
| Address Range               | Description          | Access                   |
+-----------------------------+----------------------+--------------------------+
| 0x0100 .. 0x0100+DO_NUM-1   | Toggle DO channels   | 0x05 write only          |
+-----------------------------+----------------------+--------------------------+

Write 0xFF00 to address 0x0100 + channel_index to toggle that output channel.
Writing 0x0000 is accepted but does not toggle the output.

6. Discrete Inputs (Function Code 0x02)
---------------------------------------

+------------------------+----------------------+-----------------------------+
| Address Range          | Description          | Access                      |
+------------------------+----------------------+-----------------------------+
| 0 .. DI_NUM-1          | DI input channels    | 0x02 read                   |
+------------------------+----------------------+-----------------------------+

DI inputs are active-low in the firmware mapping:

- Hardware low / active input returns 1
- Hardware high / inactive input returns 0

7. Holding Registers (Function Codes 0x03, 0x06, 0x10)
------------------------------------------------------

7.1 DAC Output Registers
------------------------

+------------------------+----------------------+-----------------------------+
| Address Range          | Description          | Access                      |
+------------------------+----------------------+-----------------------------+
| 0 .. DAC_NUM-1         | DAC output channels  | 0x03 read, 0x06/0x10 write  |
+------------------------+----------------------+-----------------------------+

DAC write value range: 0 .. 255.

Function code 0x10 supports only this DAC register range.

7.2 IR/RF Control Registers
---------------------------

+----------+-------------+----------------------+-----------------------------+
| Address  | Name        | Description          | Access                      |
+----------+-------------+----------------------+-----------------------------+
| 0x0040   | IR_SEND     | Send learned IR slot | 0x03 read, 0x06 write       |
| 0x0041   | IR_LEARN    | Learn IR slot/port   | 0x03 read, 0x06 write       |
| 0x0042   | IR_DELETE   | Delete IR slot       | 0x03 read, 0x06 write       |
| 0x0050   | RF_SEND     | Send learned RF slot | 0x03 read, 0x06 write       |
+----------+-------------+----------------------+-----------------------------+

IR_SEND:

- Value: IR memory slot index
- Valid range: 0 .. IR_MEM_NUM-1

IR_LEARN:

- High byte: IR memory slot index
- Low byte: IR send port number, starting from 1

IR_DELETE:

- Value: IR memory slot index
- Valid range: 0 .. IR_MEM_NUM-1

RF_SEND:

- Value: RF memory slot index
- The selected RF slot must exist and be learned

These registers exist only on board variants with the corresponding IR/RF
feature enabled. Otherwise accesses return an illegal data address exception.

7.3 Energy Measurement Registers
--------------------------------

Energy data is exposed as read-only Holding Registers and is read with function
code 0x03.

Each energy chip uses 68 holding registers. The base address is:

  base = 100 + chip_index * 100

where chip_index starts from 0.

+--------------+----------------+----------------+--------------------------+
| Offset Range | Parameter      | Format         | Resolution / Notes       |
+--------------+----------------+----------------+--------------------------+
| 0 .. 19      | RMS_1..RMS_10  | uint32 CDAB    | Current in A * 1000      |
| 20 .. 39     | WATT_1..WATT_10| int32 CDAB     | Power in W * 10          |
| 40 .. 59     | Energy_1..10   | float32 CDAB   | Energy in kWh            |
| 60 .. 61     | Energy_Sum     | float32 CDAB   | Total energy in kWh      |
| 62           | RMS_V          | uint16         | Voltage in V * 100       |
| 63           | Period         | uint16         | Frequency in Hz * 100    |
| 64 .. 65     | TPS1           | float32 CDAB   | Temperature in deg C     |
| 66 .. 67     | PF             | float32 CDAB   | Power factor             |
+--------------+----------------+----------------+--------------------------+

Per-channel offsets:

+----------------+----------------+----------------+--------------------------+
| Channel        | Current Offset | Power Offset   | Energy Offset            |
+----------------+----------------+----------------+--------------------------+
| 1              | 0              | 20             | 40                       |
| 2              | 2              | 22             | 42                       |
| 3              | 4              | 24             | 44                       |
| 4              | 6              | 26             | 46                       |
| 5              | 8              | 28             | 48                       |
| 6              | 10             | 30             | 50                       |
| 7              | 12             | 32             | 52                       |
| 8              | 14             | 34             | 54                       |
| 9              | 16             | 36             | 56                       |
| 10             | 18             | 38             | 58                       |
+----------------+----------------+----------------+--------------------------+

For 32-bit integer and float values, read two consecutive registers. The lower
16-bit word is returned first, followed by the upper 16-bit word.

Examples:

- Chip 1 current channel 1: read holding registers 100 and 101
- Chip 2 power channel 1: read holding registers 220 and 221
- Chip 1 voltage: read holding register 162
- Chip 1 frequency: read holding register 163

8. Input Registers (Function Code 0x04)
---------------------------------------

+-------------------------------+----------------------+--------------------------+
| Address Range                 | Description          | Format                   |
+-------------------------------+----------------------+--------------------------+
| 0 .. ADC_NUM-1                | ADC input channels   | uint16 raw ADC value     |
| 0x0100 .. 0x0100+SENSOR_NUM-1 | Temperature sensors  | int16, deg C * 10        |
| 0x0120 .. 0x0120+SENSOR_NUM-1 | Humidity sensors     | int16, %RH * 10          |
+-------------------------------+----------------------+--------------------------+

If a temperature or humidity sensor is invalid or not present, the returned
value is 0x7FFF.

9. Board-Dependent Limits
-------------------------

The following symbols depend on the compiled board model:

- DO_NUM: number of digital outputs
- DI_NUM: number of digital inputs
- DAC_NUM: number of DAC outputs
- ADC_NUM: number of ADC inputs
- SENSOR_NUM: maximum temperature/humidity sensor slots
- ENERGY_NUM: number of energy measurement chips

N-series energy chip bases:

+-------+------------+--------------------------------------+
| Board | ENERGY_NUM | Energy Holding Register Bases        |
+-------+------------+--------------------------------------+
| N10   | 1          | 100                                  |
| N20   | 2          | 100, 200                             |
| N30   | 3          | 100, 200, 300                        |
| N60   | 6          | 100, 200, 300, 400, 500, 600         |
+-------+------------+--------------------------------------+

10. Exception Codes
-------------------

+----------------+----------------------------+-------------------------------+
| Exception Code | Name                       | Meaning                       |
+----------------+----------------------------+-------------------------------+
| 0x01           | Illegal Function           | Unsupported function code     |
| 0x02           | Illegal Data Address       | Unsupported address/range     |
| 0x03           | Illegal Data Value         | Invalid value or quantity     |
| 0x04           | Slave Device Failure       | Runtime failure or overflow   |
+----------------+----------------------------+-------------------------------+

11. Request Size Limits
-----------------------

- Read coils/discrete inputs: quantity 1 .. 2000
- Read holding/input registers: quantity 1 .. 125
- Write multiple coils: quantity 1 .. 1968
- Write multiple registers: quantity 1 .. 123