01-19-2025, 10:10 AM
Here,
Board : K868-A16
Firmware : v2.2.12
Firmware : v2.2.12
Modbus CRC mistake
|
for example, if you want turn ON output1,output3, others all off
send:01 0F 00 00 00 10 00 05 BF 01 receive:01 0F 02 00 00 BB 14 note about the "send" command: 01: address 0F: functon code 00 00: address 00 fixed 00 10: because KC868-A16 have 16 channel output, so it's 0x10 00 05: means OUTPUT1, OUTPUT3: ON, others: OFF BF 01: CRC
Ok, it works for you.
but for me it is not the modbus standard, the "ByCout" byte is missing I have been using my software for over 20 years and it works with all PLCs. Here is an example with a Twido PLC SLave :1 Cf : F Adress : 0 0 Nb : 8 BYTE Count : 1 CRC : BE D5
Board : K868-A16
Firmware : v2.2.12
01-21-2025, 11:02 PM
can you let your software output command remove "BYTE Count"? it MUST need included.
01-25-2025, 04:07 PM
Hello
By going outside the Modbus standard, without the Bycout, it works. So I can't use this product with (CF15) on products that respect the standard like Schneider PLCs.
Board : K868-A16
Firmware : v2.2.12
01-26-2025, 12:25 AM
If you make bulk purchases, you can design a new firmware about it based on KC868-A16v3 new PCB.
01-26-2025, 09:49 AM
I don't understand well. With the new card I can modify the firmware of the card (your firmware) to adapt the protocol?
Or you can modify it for me?
Board : K868-A16
Firmware : v2.2.12
my means, if you order new board at a large number in future, we can modify the firmware.
02-01-2025, 10:46 AM
I have a problem with the CF15
Can you try to write 8 bits (output 0-7) when I do this, in fact it writes on outputs 8-15 Or you always have to work with 2 bytes so output 0-15
Board : K868-A16
Firmware : v2.2.12 |