Clarification on CT Clamp Sensor Input Assignments for Split-Phase Monitoring
#2
Yes, you are right. M30 use 3pcs of BL0910 energy chip. every chip manager 10 CT sensors and one VOLTAGE input.
so one chip calculate the power and energy by VOLTAGE and CT current.
so you use "Inputs 1–10 assigned to Phase A (L1)" is correct.
for example, not use CT1 with L2, CT1 MUST work with L1, so that the power and energy data is correct.