(02-17-2022, 11:18 PM)ahmedk4444@yahoo.com Wrote: Back to your answer for question 2
My load is single phases and the source is 3 phases abd it must balanced to the 3 phases however each liad us 3A orless then no need to connect through contactor and i will use the KC-868-H32B output directly to the load, the 32 channel are 4 terminal blocks each are 8 channels what i asking for to split the 8 channel for each block to 3 phases by divided into i.e phase R 2 ch phase Y 3 channel , phase B 3 channel, is it applicable to do this?
Important question here ,you adviced to connect RC snapper if use controller KC-868-H32B
How i can connect the RC snabber if connect load directly to controller output?
Last but not least it has mentioned that max ampere for each channel is 10 A max, ehy you mentioned max 3 A per Channel?
1. yes, you can do that, it's correct. balanced to the 3 phases.
2. if your H32B relay output connect to AC contactor (because it have a coin will generate interference, so we need to use RC snubber to kill it) , if you use H32B output directly connect to a lamp, i think it can work without RC snubber. RC snubber is a way to reduce interference.
3. H32B use 10A relay inside, but actually if your load work current <4A is safety, large current, we suggest add contactor for long life , it will be better.