Just i would like to add and correct me if i'm wrong
If the liad of lighting and shutters are 220v - 3-4 A each i suggest Kc868-HxxB
The terminal output can connect to 220 source and control llight and shutters, if your liad or part of it need more than 19A , 16A or more then you need to split the low loads to B type and higher liad to BS type and add the E16 module that contain relay with 12 v coil and use the dry contact for high ampere load.
Or
Use B type for all and high amp load use contactors with 220 v coil.
If the liad of lighting and shutters are 220v - 3-4 A each i suggest Kc868-HxxB
The terminal output can connect to 220 source and control llight and shutters, if your liad or part of it need more than 19A , 16A or more then you need to split the low loads to B type and higher liad to BS type and add the E16 module that contain relay with 12 v coil and use the dry contact for high ampere load.