KC868-A8 - question regarding safety shutdown
#4
1. But what does the board do if the Lan connection is gone. Do the relais and states just stay as they are or ist there also a way to shut all relais down ?

-->relais and states just stay as they are, no changes, will not all off.

2. What do you mean by use a digital input to turn off all relais (where should the signal come from)? How could that be realized?

--> my means, digital input can connect with push button, define any fucntion you wanted.

3. My idea could be to built something like a watchdog -> for example send e.g. every 5 seconds a "ping" to the KC868 board. And if this "ping" is not there the board shuts down all relais. Is that possible (maybe also via ethernet) ? Perhaps the same could be done the other way round.

--> do you want auto turn all relay off when network disconnected?

4. My idea could be to built something like a watchdog -> for example send e.g. every 5 seconds a "ping" to the KC868 board. And if this "ping" is not there the board shuts down all relais. Is that possible (maybe also via ethernet) ? Perhaps the same could be done the other way round.

--> what software you will use? home assistant? if you have a server, you can do that.
Reply