(11-08-2023, 06:05 AM)admin Wrote: first item is when 0mA's value.
second item is when 20mA's value.
Hi @admin,
I tested what you say with signal generator and values are not coincident.
Here the step by step of what I tested (I will put the picture number and an explanation at the side):
01 = Configure ADC1
02 = Inside ADC1 I write unit in mA and put the same 0 to 20mA value of the analogue entrance. Press the button "SETTING" to save the configuration.
03 = You can see on "Monitor" the values have been confirmed correctly.
04 = I send 4.00 mA and I read 3.00 mA on webpage.
05 = I send 12.00 mA and I read 10.45 mA on webpage.
06 = I send 20.00 mA and I read 18.74 mA on webpage.
07 = Configure ADC3. Inside ADC3 I write unit in V and put the same 0 to 5V value of the analogue entrance.
08 = You can see on "Monitor" the values have been confirmed correctly.
09 = I send 5.00 V and I read 5.00 V on webpage. Perfect.
10 = I send 3.15 V and I read 3.13 V on webpage. Perfect. The difference is totally normal.
Can you let me know if the test I did is correct?
Can you help me solve this problem so scale is coincident with what we read?
Thank you.