M30 does not correctly read power and energy
#11
(05-07-2024, 10:22 PM)admin Wrote: you can't chnage the value of CT sensor, just chose a suitable CT sensor. here have different SKU of CT sensor: https://www.aliexpress.com/item/3256805341385666.html

Now I am using 30A 1v CT sensor, still the current and watt values are wrong.
Reply
#12
I am using 30A 1V CT sensor, still the current and watt values are wrong. 
If CT values cannot be changed how the board detect the value of CT sensor? Each sensor will produce 1V at its max current. I am confused.
Reply
#13
if your load is 15A, you can chose 20A CT version, just nearby the value is better.
Reply
#14
(05-08-2024, 06:28 AM)admin Wrote: if your load is 15A, you can chose 20A CT version, just nearby the value is better.

I understand what you said but my submersible pump at starting draws 25A and in running 15-16 A, that is why I am using 30A 1V CT sensor.
I am bit worried about using this board to monitor my energy usage because few of my automations relay on the reading of M30.
Reply
#15
do you use home assistant software?
Reply
#16
(05-08-2024, 08:00 AM)admin Wrote: do you use home assistant software?

Yes, I am using home assistant.
Reply
#17
if you are using home assistant, you can calibrate the values on yaml file.
now we use this "coefficient", you can change it according to your data.
filters:
- multiply: 0.00098
Reply
#18
(05-08-2024, 08:45 AM)admin Wrote: if you are using home assistant, you can calibrate the values on yaml file.
now we use this "coefficient", you can change it according to your data.
    filters:
      - multiply: 0.00098

Thank you for your reply, Sure I will try and update you.
Reply
#19
ok, you just replace the new number with 0.00098
just you need test by your board.
Reply