02-14-2024, 11:23 AM
yes, you are right, A16 support use by DC24v power supply. DC12v is one of case.
KC868-A16 wiring diagram
|
02-14-2024, 11:23 AM
yes, you are right, A16 support use by DC24v power supply. DC12v is one of case.
02-14-2024, 11:26 AM
02-15-2024, 01:03 AM
you are welcome.
06-03-2024, 11:19 AM
For the logical input, I need to use the variant: DC +8-12V is logical "1".
How should I connect the +?V DC voltage input to the A16 input? Can I (must) use the same +12VDC source as the A16 module power supply? Where do I connect the GND on the input terminals?
06-03-2024, 12:15 PM
use by DC12-24v power supply for KC868-A16
digital input can use dry contact signal or DC12-24V.
06-03-2024, 02:08 PM
OK, so I am going use one 24V DC source to power A16 and to (from the same source) +24V to the logic input terminals.
06-03-2024, 10:02 PM
sure , no problem.
06-04-2024, 12:37 PM
I tested both variants on Digital Input:
1/ use dry contact signal [input is connected to GND terminal by button] => logical 1... that's OK. 2/ use of DC +12 [the input is connected by a button to the +12V source of the A16 module] => no change in the input is shown in the Monitor screen. ..here is the error. according to your description, it should respond to +12V DC (or +24V). where is the problem? please, send me the wiring diagram for variant 2/.
06-04-2024, 10:21 PM
0v = trigger
12v or 24v = NOT trigger
I don't understand your answer.
In the description of the device A16, you have the input DC 8-12V is logical "1". I bought the A16 mainly because of this information. I have +12V DC voltage outputs from other devices that signal logic "1" and I need to measure them and convert them to HomeAssistant. |