I produced nodered diagram(for test) to control h32b controller. for test, i want to control 3 realys by one switch.
the problem is :
when i turn on the switch, i got just one relay turn on from the three relays.(they don't turn on all of them in the same time). but if i put timer for the other 2 relays, then i got all relays turn on.
Now I'm having a problem. I chaned the mode in the ethernet mode from UDP to mqtt and inserted the username and password, and saved.
there were some relays in the H32B that i set time auto off, and after changing the UDP to mqtt, I noticed that the time auto off reset to defult and now thers are no auto off relays. and also i'm not able to enter the settings by the ethernet IP address which was 10.0.0.3
1. Hold on Ethernet button on PCB, when the [yellow and white LED] all is ON, release it, then work mode in “UDP” and IP by DHCP mode;
2. use kincony scan device tool to find out controller IP address.
3. login by webpage, check what firmware version you are using? you can try to update to newest version V5.08 for KC868-H32B controller, here is download link: https://www.kincony.com/forum/showthread.php?tid=3323