KC868-A16 analog input
#1
Is it possible to connect an analog sensor with a 4-20mA output to the KC868-A16? Some say only 0-5V and some say both. If so, how please? Thanks.
Reply
#2
KC868-A16 board: analog input: A1,A2 for 4-20mA A3,A4 for 0-5v dc
Reply
#3
I have four three-phase motors and I need to read one phase of each motor. I am using the KC868-a16 and the JXK-10 CTs, two with 4-20mA output and two with 0-5V output.

The CTs have two inputs for 24V +/- power supply and two +/- 4-20mA or 0-5V outputs. In this project, I joined the "Out -" outputs of the four CTs and connected them to the analog GND of the KC868-a16. The "Out +" outputs were connected to each specific 4-20mA input A1, A2 and 0-5V A3, A4.

Is this connection correct?

KC868-a16 TC.jpg
Reply
#4
KC868-A16 not support CT clamp sensor. you need use M30 board for CT clamp.
Reply
#5
I made the connections and it's working!

The CT I'm using has a 4-20mA or 0-5V output and not AC voltage.

https://pt.aliexpress.com/item/100500613...ry_from%3A

- platform: adc
    pin: 34
    name: "A16 A2 mA"
    update_interval: 5s
    attenuation: 12db
    unit_of_measurement: mA
    filters:
      - multiply: 6.66666666
Reply
#6
ok, i see now, you are using DC CT sensor.