1: Read 4 channel analog inputs by TCP command:
Send: RELAY-GET_AI-255
Feedback: RELAY-AI-ALL,A0,A1,A2,A3,OK
A0,A1 analog input range: DC0-5V
A2,A3 analog input range: 4-20mA
example:
A0 and A1 connect with 3.3V , will feedback:
RELAY-AI-ALL,330,330,0,0,OK
A2 and A3 connect with 10mA sensor , will feedback:
RELAY-AI-ALL,0,0,455,455,OK
--------------------------------------------------------------
2: enable/disable analog inputs by TCP command:
Send: RELAY-AI_REPORT-255,1 //Enable analog input AUTO feedback
Feedback: RELAY-AI_REPORT-255,1,OK
Send: RELAY-AI_REPORT-255,0 //Disable analog input AUTO feedback
Feedback: RELAY-AI_REPORT-255,0,OK
---------------------------------------------------------------
3. Read 4 channel analog inputs by MODBUS RS485
01 03 01 2C 00 04 CRCH CRCL
Feedback: 01 03 08 A0 A1 A2 A3 CRCH CRCL
01:RS485 address ID
01 2C=300 register address
00 04 register number
example:
if A0 connect with 3.29V
Send: 01 03 01 2C 00 04 84 3C
Feedback: 01 03 08 01 49 00 00 00 00 00 00 8C DF
01 49 =329 = 3.29V
if A1 connect with 3.31V
Send: 01 03 01 2C 00 04 84 3C
Feedback: 01 03 08 00 00 01 4B 00 00 00 00 30 08
01 4B =331 = 3.31V
Send: RELAY-GET_AI-255
Feedback: RELAY-AI-ALL,A0,A1,A2,A3,OK
A0,A1 analog input range: DC0-5V
A2,A3 analog input range: 4-20mA
example:
A0 and A1 connect with 3.3V , will feedback:
RELAY-AI-ALL,330,330,0,0,OK
A2 and A3 connect with 10mA sensor , will feedback:
RELAY-AI-ALL,0,0,455,455,OK
--------------------------------------------------------------
2: enable/disable analog inputs by TCP command:
Send: RELAY-AI_REPORT-255,1 //Enable analog input AUTO feedback
Feedback: RELAY-AI_REPORT-255,1,OK
Send: RELAY-AI_REPORT-255,0 //Disable analog input AUTO feedback
Feedback: RELAY-AI_REPORT-255,0,OK
---------------------------------------------------------------
3. Read 4 channel analog inputs by MODBUS RS485
01 03 01 2C 00 04 CRCH CRCL
Feedback: 01 03 08 A0 A1 A2 A3 CRCH CRCL
01:RS485 address ID
01 2C=300 register address
00 04 register number
example:
if A0 connect with 3.29V
Send: 01 03 01 2C 00 04 84 3C
Feedback: 01 03 08 01 49 00 00 00 00 00 00 8C DF
01 49 =329 = 3.29V
if A1 connect with 3.31V
Send: 01 03 01 2C 00 04 84 3C
Feedback: 01 03 08 00 00 01 4B 00 00 00 00 30 08
01 4B =331 = 3.31V