Posts: 10,547
Threads: 1,576
Joined: Oct 2020
Reputation:
262
if your load is very small can use this relay 6A. but you should not use full of 6A, it's not safety. we suggest use 10A relay will be more safety. because if use LED, the instantaneous current is very large. we have used 5A relay in KC868-H32 (it's first version of 32 relay board), but sometimes work with LED will let the relay's contact bad.
Posts: 10,547
Threads: 1,576
Joined: Oct 2020
Reputation:
262
8 channel: 131mm*85mm weigh:327g
16 channel: 218mm*85mm weigh:327g
24 channel= 8 channel +16 channel's width
Posts: 49
Threads: 19
Joined: Jun 2021
Reputation:
0
Hi. Thanks for the valuable info!
Are there any considerations to prefer 24V DC over 12V DC for relays command (or visa-versa)? Is it significantly more reliable using 24V for some reason? (regarding the relays / the relay's circuit / the H32BS MOSFET)
Posts: 10,547
Threads: 1,576
Joined: Oct 2020
Reputation:
262
it's same. we suggest use DC12V. just sometimes if used system by DC24V, so you can chose DC24v contactor. if voltage is higher, the load current will be lower.
Posts: 10,547
Threads: 1,576
Joined: Oct 2020
Reputation:
262
11-19-2021, 12:39 PM
(This post was last modified: 11-19-2021, 12:42 PM by admin.)
sorry for the mistake for 16 channel size. next week we will update webpage.
8 channel size is 131mm*85mm