05-18-2023, 08:38 AM
OK I will try this as a test with another bulb attached but this will not help me.
Each room has only 1 dimmable bulb at no more than 10w (this is equivalent to 60w as a incandescent bulb) so if I was to change this bulb for a 17w/18w bulb (this is equivalent to a 100w bulb) the room would be to bright but you are saying your SSR will not operate correctly without 18w starting load?
Most led bulbs are between 3w to 10w so I am not sure how I can solve this problem with your SSR?
Also is the reason why when your input is not providing power to the SSR from the controller the led is still on and still very dim and never switches off?
Each room has only 1 dimmable bulb at no more than 10w (this is equivalent to 60w as a incandescent bulb) so if I was to change this bulb for a 17w/18w bulb (this is equivalent to a 100w bulb) the room would be to bright but you are saying your SSR will not operate correctly without 18w starting load?
Most led bulbs are between 3w to 10w so I am not sure how I can solve this problem with your SSR?
Also is the reason why when your input is not providing power to the SSR from the controller the led is still on and still very dim and never switches off?