Thread Rating:
  • 0 Vote(s) - 0 Average
  • 1
  • 2
  • 3
  • 4
  • 5
convert 4-20mA to 0-5v by 250 Ohm resistance for KC868-COLB/COL
#1
KC868-COL support use analog sensor that 0-5V output, if you already have 4-20mA sensor. you can use a 250 Ohm resistance connect with signal input port and GND to convert.

To convert a mA analog input signal to voltage you need to attach a inline resistor. The size of your resistor will determine the output range of your voltage. 

Resistor Calculations are as follows:

Using ohms law V = R(I)  (Voltage = Resistance * Current)


If we were to scale a 4-20mA to 1-5V

For the 0 Value: .004 Amps * 250 ohms = 1 Volt

For the Max Value: .20 Amps * 250 ohms = 5 Volts
Reply
#2
Very useful tip, thank you. Could you please add a picture of resistor installed?
Reply
#3
this is a sample for AI1 and AI3 input use by 4-20mA sensor to convert to voltage signal by 2pcs 250 ohm resistance.
   
Reply
#4
   
   
Reply


Forum Jump:


Users browsing this thread:
1 Guest(s)