Thread Rating:
  • 0 Vote(s) - 0 Average
  • 1
  • 2
  • 3
  • 4
  • 5
Maximum input current and voltage
#1
Hi,
what are the maximum voltage and current that the inputs of the KC868-M16v2 accepts?
I wish to know in order to select the most suitable CT-clamps for my power distribution box.
If this is specified somewhere, I didn't find it. If so, where is the spec sheet that mentions these values?
Thanks in advance
Reply
#2
CT clamp sensor voltage range is dc 0-1v
CT clamp sensor current range is 0-50mA
Reply
#3
Thanks for your answer.

Your answer is not 100% what I asked. But I'm guessing the rest of the reasoning. Can you confirm?

25mA and 1V are also the maximum input current/voltage that should be applied to the bourd inputs?

And therefore, selecting the right CT-clamp means that I need to select the CT-clamp with the lowest possible input current, which is higher than the highest current that I will ever monitor.
Is that correct?

Thanks again
Reply
#4
50mA and 1V are also the maximum input current/voltage that should be applied to the board inputs? Yes, here is M16 diagram: https://www.kincony.com/download/KC868-M...ematic.pdf
Reply


Forum Jump:


Users browsing this thread: